PROFIBUS Mode: Enhanced+
The Enhanced+ mode is one of the Basic/Enhanced PROFIBUS Modes available only on the RMC75P. Most users will prefer the I/O Modes instead.
Features
This mode has the following features:
RMC75 Register Addresses for PROFIBUS
When communicating over PROFIBUS, the RMC75 registers addresses use the same file:element addresses as the RMC75 IEC-61131 addresses.
For example, to read the Axis 0 Actual Position via PROFIBUS, notice that its address is %MD8.8. Therefore, the address via PROFIBUS is file 8, element 8.
Parameterization
Enhanced+ mode requires the PROFIBUS configuration and parameterization listed below. The GSD file does direct the PROFIBUS master setup software to automatically set up these values, but Delta has found several cases where it is not supported correctly or manual setup is otherwise required.
Configuration: FF DF FF
Parameters:
Prm_Data (bytes 1-7): See the PROFIBUS DP specification for details.
User_Prm_Data (bytes 8-14): 00 00 00 xx* 01 10 08
 * The xx parameter can be 00 or 01 and selects whether the least-significant word comes first (00) or most-significant word comes first (01).
Data Blocks
The Enhanced+ mode uses two fixed-length blocks of data: the Command Block and the Response Block.
ClosedCommand Block
The Command block is a block of 16 contiguous 32-bit output registers. These registers are sent from the PLC or PC to the RMC.
The Command Block has the following structure:
Register
Number
Data
Type
Description
Command Area:
Registers 0 - 5 are used for issuing commands to the RMC75. See Issue a Single Command and Issue Simultaneous Commands below for details on using these registers.
Integer
Command Register
Bit
Bit Description
31
Command Request
30
Deferred Command
29
Deferred Command
20-28
Reserved
19
Axis 3 Select
18
Axis 2 Select
17
Axis 1 Select
16
Axis 0 Select
8-15
Reserved
7-0
Command Number
1
Float
Command Parameter 1
2
Float
Command Parameter 2
3
Float
Command Parameter 3
4
Float
Command Parameter 4
5
Float
Command Parameter 5
Data Channel 0:
Registers 6 and 7 are used for reading and writing to any register in the RMC75.  See Read any Single RMC75 Register and Write to any Single RMC75 Register for details on using these registers.
6
Integer
Read/Write Register
Bit
Bit Description
31
Read/Write
30
Read/Write Request
16-29
Reserved
15-8
R/W Address File
7-0
R/W Address Element
7
Float*
Explicit Write Value
Data Channel 1:
Registers 8-15 are used for explicit reads and writes. See ReadAny Contiguous RMC75 Registers and Write Any Contiguous RMC75 Registers below.
8
Integer
Read/Write Command Register
Bit
Bit Description
31
Read/Write
30
Read/Write Request
24-29
Reserved
16-23
Count
15-8
R/W Address File
7-0
R/W Address Element
9
Float*
Explicit Write Value 0
10
Float*
Explicit Write Value 1
11
Float*
Explicit Write Value 2
12
Float*
Explicit Write Value 3
13
Float*
Explicit Write Value 4
14
Float*
Explicit Write Value 5
15
Float*
Explicit Write Value 6
*These registers are typically REAL data type (floating point), but in some cases may be DINT or DWORD  integers, such as variables declared as such.
ClosedResponse Block
The Response Block is a block of 24 contiguous 32-bit input registers (cyclic read registers). Registers 0-15 correspond to the Indirect Data Map registers 0 to 15 in the RMC75. These registers are continuously sent from the RMC75 to the PLC or PC. Registers 16-23 are for explicit reads or writes.
The Response Block has the following structure:
Register
Number
Data
Type
Description
Note:
Register 0 supplies the reading and writing acknowledge for the Command Block register 6.
Integer
Indirect Data 0 - must be mapped to Axis 0 Status bits!
Bit
Bit Description
31
Command Acknowledge
30
Read/Write Acknowledge
0-29
Axis 0 Status Bits
1
Float*
Indirect Data 1
2
Float*
Indirect Data 2
3
Float*
Indirect Data 3
4
Float*
Indirect Data 4
5
Float*
Indirect Data 5
6
Float*
Indirect Data 6
7
Float*
Indirect Data 7
Note:
Registers 8-15 are not consistentClosed A block of PROFIBUS data is called 'consistent' if it is consistent over the length of the block, rather than just over a single 8- or 16-bit data item. Consistent blocks of data will stay together through the communication, from the time it was captured in the slave device until it is delivered to the master application, whereas data from different consistent blocks could have been sampled at different times. with registers 0-7. See explanation below.
8
Float*
Indirect Data 8
9
Float*
Indirect Data  9
10
Float*
Indirect Data 10
11
Float*
Indirect Data 11
12
Float*
Indirect Data 12
13
Float*
Indirect Data 13
14
Float*
Indirect Data 14
15
Float*
Indirect Data 15
Note:
Register 16 supplies the reading and writing acknowledge for registers 17-23.
16
Integer
Read/Write Acknowledge Register
Bit
Bit Description
30
Note:
The entire Command Register 8 is echoed to this Read/Write Acknowledge Register. Typically, bit 30 is the only bit used.
17
Float*
Explicit Read Data 0
18
Float*
Explicit Read Data 1
19
Float*
Explicit Read Data 2
20
Float*
Explicit Read Data 3
21
Float*
Explicit Read Data 4
22
Float*
Explicit Read Data 5
23
Float*
Explicit Read Data 6
A Note about PROFIBUS Consistency
Registers within a consistent block are all updated at the same time.  Notice that the Response Block area is divided into two consistent blocks.  Therefore, the first eight (8) registers may have been updated at a different time than the last eight (8) registers.  This is important because command and read/write synchronization use the first register, and therefore only the following seven (7) registers are guaranteed to have been updated at the same time as this synchronization register.
For example, suppose a PLC issues a command to axis 1 and then needs to wait for it to get in position.  To do this, the PLC must issue the command, wait for the command to be received, and finally check the axis's In Position status bit.  However, if the Axis 1 Status Bits register is placed in the second block of registers, then even after the Command Acknowledge bit matches the Command Request bit, indicating that the command was received, we have no way of knowing whether the Axis 1 Status Bits register was read from the controller before or after the command was issued, and thus could provide the In Position bit from before the command was issued.
In short, do not put any registers that depend on a command being issued—such as axis Status Bits, Error Bits, or Command Position—or the Read Response—which is tightly coupled to the Read/Write Acknowledge bit in register 0—in the second block of registers.
Configuring the Data
ClosedSetting up the Indirect Data Map
The Response Block continuously returns the values from the RMC75 Indirect Data registers 0-15. These registers, in turn, can be mapped to any registers in the RMC75. Thereby, the values from the selected registers in the RMC75 can be read from and written to by writing to  and reading from the Indirect Data registers.
To set up the Indirect Data Map:
  1. In the Project pane, double-click Address Maps, then click Indirect Data Map.
  2. In the Register column of the first Indirect Data Map entry, type "%MD8.0" and press Enter. This will map Axis 0 Status Bits register to the first item in the Indirect Data Map. Basic mode requires that the first item in the Indirect Data Map contains the Axis 0 Status Bits register.
  3. For each of the remaining Indirect Data Map entries 1-15, enter the desired register to map to each. To do this, click the cell in the Register column, click the ellipsis button (), then browse to the desired register.
    Note:
    Response Block registers 8-15 are not consistentClosed A block of PROFIBUS data is called 'consistent' if it is consistent over the length of the block, rather than just over a single 8- or 16-bit data item. Consistent blocks of data will stay together through the communication, from the time it was captured in the slave device until it is delivered to the master application, whereas data from different consistent blocks could have been sampled at different times. with registers 0-7. Because of this, registers 8-15 should not be used for tight synchronization with registers 0-7. The following registers should not be placed in Indirect Data Map registers 8 to 15:
    - Read Response, because it is tightly coupled with the Read/Write Acknowledge bit in register 0.
    - Status and Error bits, Actual Position, Command Position, because these depend on the command being issued.
  4. If you wish to add additional read capability, one of the Indirect Data Map registers should be mapped to the Read Response register. Then, the corresponding register in the Response Block will return the value of a read from any single register in the RMC75 at any time. See Read any Single RMC75 Register below. Notice that this is probably unnecessary because this mode already enables you to read from seven contiguous registers. See Read any Contiguous RMC75 Registers below.
Example
Requirements
First, the user lists the desired registers to read from the RMC75:
In addition, the user would like to read some other registers occasionally.
Implementation
The user chose to set up the Indirect Data Map like this:
Using the Data Blocks
ClosedIssue a Single Command
To issue a command, set up the contents of the first six registers of the Command Block, and when complete, toggle the Command Request bit in the first Command Block register.
Notice that commands with more than 5 command parameters cannot be issued via PROFIBUS. To issue such commands, include them in a user program and issue a command via PROFIBUS to start the user program.
To issue a single command to the RMC75, use the following steps:
  1. Wait until the Command Request bit in the Command Register (0) of the Command Block is equal to the Command Acknowledge bit in register 0 of the Response Block.  If they are not equal, the RMC is currently processing a command request.
  2. Enter the command number in bits 0-7 of the Command Register (0) of the Command Block.
  3. If the command has any parameters, put them in registers 1-5 of the Command Block.
  4. Clear the Deferred Command bits.
  5. Set the desired Axis Select bit in the Command Register. The command will be sent simultaneously to each axis you select.
Note:
Using this method, you can send a single command to multiple axes simultaneously. You cannot send different commands to multiple axes simultaneously. To send different commands to multiple axes simultaneously, see the Issue Simultaneous Commands section below.
  1. Toggle the Command Request bit.
  2. Wait until the Command Request bit is equal to the Command Acknowledge bit.  When they are equal, the RMC75 has received the command.
NOTE:
Until the Command Acknowledge bit matches the Command Request bit, the Input Data registers, including the Status Bits registers, do not reflect having received the command.
Example
A Move Absolute (20) command is issued using the PROFIBUS Command Block.  Until the
Command Requestbit matches the Command Acknowledgebit after the Command Requestbit has been toggled, the In Positionbit should not be checked as it may still be set for the previously requested move.  Once the Acknowledgetoggles to match, the In Positionbit will have been cleared and when it is set, it is due to the new command being complete.  Similar synchronization issues are resolved in the same way with other status bits and registers.
ClosedIssue Simultaneous Commands
Although only one command may be sent at a time to the RMC75P via PROFIBUS, it is possible to simultaneously issue different commands to several axes by using deferred commands. Deferred commands are stored in the PROFIBUS command buffer until all deferred commands are received. They are then executed simultaneously. Bits 30 and 29 in the Command Data Register of the Command Block define the deferred status of each command issued. The bits are used as follows:
Bit
30
Bit
29
Action
Single Command: When both bits are zero, the command is not deferred. The command is executed normally. If the PROFIBUS command buffer contains any commands, an error is logged in the Event Log and the commands are removed from the command buffer without being executed.  The new command is still issued.
1
Last Deferred: This command and any deferred commands in the PROFIBUS command buffer are executed simultaneously.
1
First Deferred: This command is placed as a deferred command in the PROFIBUS command buffer, but is not otherwise processed.  If the command buffer already contains commands, an error is logged in the Event Log and the commands are removed from the command buffer without being executed.  The new deferred command is still placed in the command buffer.
1
1
Middle Deferred: This command is placed as a deferred command in the PROFIBUS command buffer, but is not otherwise processed.  This deferred command type allows other deferred commands to be in the command buffer, although they are not required to be there.  Note that for a 2-axis controller, this deferred setting will not be used because there can only be a first and last deferred command.
Multiple deferred commands cannot be issued to the same axis. That is, if a deferred command is issued to an axis that already has a deferred command, an error is logged in the Event Log and the previous command is overwritten without being executed.
ClosedRead Any Single RMC75 Register
Registers 0-15 of the Response Block return the values from 16 registers, which must be determined when setting up the communications. However, it is possible to set up one of the registers 1-7 in the Response Block to return the value of a read from any single register in the RMC75.
When a read is requested from any single register in the RMC75, the response from this single-register read will be placed in the Axis 0 Read Response register. In order to see the response from the PROFIBUS, you must map the Axis 0 Read Register into one of the Indirect Data Map registers.
Notice that the copy from the requested register into the Axis 0 Read Response register only occurs once, and therefore you will not see the value continuously updating like the other Response Block registers.
To read any single register from the RMC75, use the following steps:
To further clarify the ordering, keep these basic rules in mind:
ClosedRead Any Contiguous RMC75 Registers
To read any contiguous RMC75 registers, use the Command Block register 8 and the Response Block registers 16-23.
To read any contiguous RMC75 registers, use the following steps:
ClosedWrite to Any Single RMC75 Register
To write to a single RMC75 register, use the Command Block register 6 and the Response Block register 0. Register 0 of the RMC75 Indirect Data Map must be mapped to the Axis 0 Status Bits register.
To write to the RMC75, use the following steps:
Note:
The RMC75 sets the Read/Write Acknowledge bit equal to the Read/Write Request to the acknowledge that the write was processed. In addition, the RMC75 also places the write value in the Read Response register. This provides a simple method of verifying that the write was completed.
ClosedWrite to Any Contiguous RMC75 Registers
To write to any contiguous RMC75 registers, use Command Block registers 8-15 and Response Block register 16.
Debugging
ClosedUsing the Event Log for PROFIBUS
The Event Log can record every change in the PROFIBUS data received by the RMC75P. This is the data in the Command Block. It does not record the data in the Response Block, which is sent by the RMC75P. The Event log displays the received data in hexadecimal format.
The Event Log can log an entry when any of the following occurs:
Tip:
In some cases, a request can be made, but nothing happens. This is probably caused by one of the following:
- A command was requested, but no Selected Axis bit was set.
- A read or write of multiple registers was requested, but the Count was set to 0.
The Event Log labels the logged entries in the following manner:
Debugging the Command Area Data
The Event Log displays the Command Area data in the following order:
Cmd Register, Cmd Parameter 1, Cmd Parameter 2, Cmd Parameter 3, Cmd Parameter 4, Cmd Parameter 5
ClosedExample:
Assume a Move Absolute command has been issued to the RMC75 via PROFIBUS. The Event Log may look like this:
Steps 28-31 show how the command parameters are changing. The command word shows the command that will be issued, (hexadecimal 14 is 20 in decimal), and the command select bit ( the 1 in the middle of the word).
In step 33, bit 31 of the Command Register changed, which then issued the move command.
Debugging Data Channel 0
The Event Log displays the Data Channel 0 data in the following order:
Read/Write Register (register 6), Explicit Write Value (register 7)
ClosedExample:
Assume a value of 46.2 was written to %MD56.0 via PROFIBUS. The Event Log may look like this:
Step 38 shows that the File is 56 (38 in hexadecimal), bit 31 is set to 1 for a write. The Explicit Write register contains the write value 46.2, but it is very difficult to decipher a float value from its hexadecimal representation.
Step 39 shows that the Read/Writer Request bit changed, which  requested the write.
Debugging Data Channel 1
The Event Log displays the Data Channel 1 data in the following order:
Read/Write Command Register (register 8), Explicit Write Value 0, Explicit Write Value 1, Explicit Write Value 2, Explicit Write Value 3, Explicit Write Value 4, Explicit Write Value 5, Explicit Write Value 6
ClosedExample:
Assume 3 values were written to 3 registers beginning at %MD56.10. The Event Log may look like this:
In step 43, the Element is 10 (A in hexadecimal).
In step 44, the File is set to 56 (38 in hexadecimal).
In step 45, the count is set to3.
In steps 46 to 48, the write values are entered.
In step 49, bit 31 is set to 1 for a write.
In step 50, bit 30 is toggled to request the write.
Basic/Enhanced PROFIBUS Modes | PROFIBUS Configuration | PROFIBUS-DP Overview