For general specifications on the RMC, see RMC100 Specifications.
Encoder
Axes |
Two per module |
Encoder Inputs |
RS422 differential receiver (can also be used as TTL) |
Input Impedance |
215 W Differential Input 430 W Single-Ended Input
ESD Protection |
15 kV |
Max. Encoder Frequency |
4,000,000 quadrature counts/second |
Index (Z) Response Time |
125 nanoseconds |
Inputs and Outputs
Fault Inputs, Home Inputs, and Limit Inputs |
2.7 V @ 2.8 mA typical (3.2 V @ 3.5 mA max) threshold, 26.4 V maximum input voltage, 500 VDC isolation, compatible with most limit switches, TTL, and CMOS outputs |
Home and Registration Input Response Time |
50 microseconds |
Home Options |
Any combination of Index (Z) input and Home (H) input |
Amplifier Enable Output |
Solid State relay, 50 W, 30 V, 100 mA |
Drive Outputs
Range |
±10 V @ 5 mA (2 kW or greater load) (For current drive, use the VC2100 accessory: |
Tolerance |
At 10 V: +200 mV, -100 mV |
Resolution |
12 bits for revisions 1, 2, and 4 |
Output Isolation |
500 VDC, optically isolated |
Overload Protection |
One-second short-circuit duration |
Overvoltage Protection |
Outputs are protected by clamp diodes |