Auto Stop
Default: 0x1FE0 (Soft Stops enabled, Hard Stops enabled for Transducer Errors)
Click here for the Auto Stop Bit Map
The Auto Stop parameter controls the action taken on the rising edge of any of the axis' error bits (the eight (8) most-significant bits in the Status word listed below). The user has control over which error bits cause which levels of stop, or whether an error will cause a stop at all. The default setting of all the AutoStops is Hard Stop, as described below.
During startup and tuning, you will typically need to set some AutoStops to Status Only to keep halts from interfering with the tuning. After completeing the startup procedure, make sure to set the AutoStops to setting that are safe for the machine operation.
Auto Stops are always active unless the axis is in Open Loop, in which case no Auto Stops will be triggered even though error bits may be set.
Note: AutoStops will not occur if the axis is in Open Loop!
The eight (8) most-significant bits in the Status word, as listed below, are the error bits, with the exception of the Home Input status bit for Quadrature axes with Analog (QUAD) or Stepper (STEP) output:
Fault
QUAD
STEP
All Others
7
Encoder Error/Fault
Encoder Error/Fault
No Transducer
6
Extend Limit
Extend Limit
Transducer Noise
5
Retract Limit
Retract Limit
Transducer Overflow
4
Overdrive
Overdrive
Overdrive
3
Parameter Error
Parameter Error
Parameter Error
2
Home Input
Home Input
Pos./Press. Overflow
1
Integrator Windup
Compensation Timeout
Integrator Windup
Following Error
Following Error
Following Error
The available actions for each fault are listed below:
To view or change the Auto Stop parameter value, open the Auto Stop popup editor in RMCWin using one of the methods described in Using Popup Editors. Select the desired action for each fault type and click OK. Changes to this parameter do not take effect until you issue a Set Parameters (P) command.
Manual Parameter Entry
This parameter can also be edited manually, but this is discouraged since it is much easier to use the popup editor. You can enter hexadecimal numbers by typing a leading 0x, as in 0x1FE0. Each of the eight faults listed above has two bits assigned to it, labeled S and H in the table below:
Bit
Description
Bit
Description
15
Fault 7 - Bit S
7
Fault 7 - Bit H
14
Fault 6 - Bit S
6
Fault 6 - Bit H
13
Fault 5 - Bit S
5
Fault 5 - Bit H
12
Fault 4 - Bit S
4
Fault 4 - Bit H
11
Fault 3 - Bit S
3
Fault 3 - Bit H
10
Fault 2 - Bit S
2
Fault 2 - Bit H
9
Fault 1 - Bit S
1
Fault 1 - Bit H
8
Fault 0 - Bit S
Fault 0 - Bit H
For each fault, the two bits in the Auto Stop parameter define the action as follows:
Bit H
Bit S
Description
Status Only
1
Soft Stop
1
Hard Stop
1
1
Disable Drive
If you select Status Only for a fault that cannot use that action, then the axis will use a Soft Stop action for that fault. Similarly, if you select Disable Drive for a fault on an axis that does not have an Amp Enable output, the axis will use the Hard Stop action for the fault.