Set Pressure Ramp Time Command
Character: \
Decimal: 92
Hexadecimal: 0x5C
Command Value: Milliseconds
This command sets the Ramp Time value to the Command Value. Refer to Ramp Time for details on this field.
The change in the Ramp Time value will take affect immediately if the axis is regulating pressure at the time. The remaining ramp time is taken as a fraction of the entire Ramp Time and multiplied by the new Ramp Time.
Example:
Suppose that an axis was to ramp the pressure from 2000psi to 2200psi over two seconds. Therefore, the Ramp Time would have been 2000 milliseconds. Suppose that one and a half seconds into the ramp, this command is issued with a Command Value of 4000. Therefore, because one fourth of the original Ramp Time was remaining, one fourth of the new Ramp Time (one fourth of 4000 milliseconds or 1000 milliseconds) will remain. So, the rest of the ramp will take a full second.