Link Type: |
LoopStart (#, hex 0x23, dec 35) |
Link Value: |
Number of loop iterations |
Range: |
0 to 65,535 |
Note: This feature is available only in RMC100 CPU firmware version 19980811 and later.
Note: This link type cannot be used with the Poll (?) command.
The LoopStart (#) and LoopEnd (-) link types are used together to create loops in the Event Step table. The Link Value of the LoopStart link type indicates how many iterations you want through the loop. The LoopStart link type jumps immediately to the step indicated by the Link Next. This should typically indicate the step of the LinkEnd link type.
The LoopEnd link type tests the loop counter to see if it zero. If it is zero then the next step—not the step specified in the Link Next field—will be executed. If the loop counter is not zero then it is decremented by one and the step specified in the Link Next field is jumped to. The Link Value on the LoopEnd link type is ignored and should be set to zero (0).
Example:
The following example executes steps 2 though 5 three times. After the third loop step 7 is executed.
Step 1 |
Step 2 |
Step 3 |
Step 4 |
Step 5 |
Step 6 |
Mode |
0x0081 |
0x0081 |
0x0081 |
0x0081 |
0x0081 |
0x0081 |
Accel |
100 |
100 |
100 |
100 |
100 |
100 |
Decel |
100 |
100 |
100 |
100 |
100 |
100 |
Speed |
10000 |
10000 |
10000 |
10000 |
10000 |
10000 |
Command Value |
4000 |
10000 |
10000 |
4000 |
4000 |
4000 |
Command |
G |
G |
Commanded Axes |
Default |
Default |
Default |
Default |
Default |
Default |
Link Type |
LoopStart |
BitsON |
DelayMS |
BitsON |
DelayMS |
LoopEnd |
Link Value |
3 |
1000 |
1000 |
Link Next |
6 |
3 |
4 |
5 |
6 |
Under Link Type, select Loop.
Under Link Condition, select Start a Loop or End a Loop.
If you selected Start a Loop, enter the number of iterations you want to use.
To start a loop, enter '#' for the Link Type. To end a loop, enter '-' for the Link Type.
If you started a loop, enter the number of iterations in the Link Value. Otherwise enter 0 in the Link Value.