Format: 0AAA RRRR 1110 NNNN
R Used for Status Area Request
N Used for Command Index described below
A Used only by Communication Digital I/O; 0 for PROFIBUS-DP
These commands let you change an event parameter’s value across a range of steps in a single scan. The format of the Command Register for the Event Step Edit commands is given below:
1111|11 | |
BIT #5432|1098|7654|3210
HEX |SAR |CMND|INDX
VALUE -------------------
0XE0 0AAA|XXXX|1110|0000 Start Step Number (0 to 255)
0XE1 0AAA|XXXX|1110|0001 End Step Number (0 to 255; > E0)
0XE2 0AAA|XXXX|1110|0010 Parameter to Modify (0 to 7)
0XE3 0AAA|XXXX|1110|0011 Value to be Used
For command types 0XE0 and 0XE1, the command data represents a step number. For command type 0XE2, the command data represents the field that will be modified by 0XE3. Use the following table to select a field:
0XE2 DATA |
STEP FIELD |
3 |
4 |
5 |
6 |
7 |
To edit the Event Step table, each of these commands must be issued once to initialize the parameters; this will take four scans. Once the beginning step number, the ending step number, and the parameter to be changed have been defined, all the steps can be changed in a single scan by sending 0XE3 command with the new parameter value. All four of these commands must be sent on the same axis.
If you have a step table that is 100 steps long and you want to change the time delay link value in each step, it would take 100 scans by using the Event Step Transfer commands. If the scan time is 20ms, this would take 2 seconds. By using the Event Step Edit commands, it would take 80ms for the first change (four scans times 20ms/scan) and only 20ms for another change.
Assuming we want to modify steps 0 to 99 and the new link value will be 500, the following commands would be sent:
First scan: |
O+1 |
0XE0h |
(Set Start Step Number) |
O+2 |
(Start Step Number of 0) |
Second scan: |
O+1 |
0XE1h |
(Set End Step Number) |
O+2 |
99 |
(End Step Number of 99) |
Third scan: |
O+1 |
0XE2h |
(Set Parameter to Modify) |
O+2 |
7 |
(Select Link Value) |
Fourth scan: |
O+1 |
0XE3h |
(Set Actual Value) |
O+2 |
500 |
(Link Value itself) |
Example for Digital I/O:
First scan:
0000|XXXX|1110|0000 (0XE0) Set start step number
Receive after Acknowledge:
XXXX|XXXX (XX) Low byte of requested data
0000|0000|0000|0000 (0000) Start at step number 0
XXXX|XXXX (XX) High byte of requested data
Second scan:
0000|XXXX|1110|0001 (0XE1) Set End Step Number
0000|0000|0110|0011 (0063) End Step Number of 99
Third scan:
0000|XXXX|1110|0010 (0XE2) Set Parameter to Modify
0000|0000|0000|0111 (0007) Select Link Value
Fourth scan:
0000|XXXX|1110|0011 (0XE3) Set actual value
0000|0001|1101|1000 (01D8) Link Value (500)