D24 Wiring

This topic covers the wiring of the RMC200 D24 Module. See Wiring Guidelines for general wiring information.

The D24 discrete I/O are organized into 4 sections:

 

DI/O #

Features

Group A

0-7

Input or output – nominal 24V. Each I/O points is individually software-configurable as an input or output. Each group is isolated. Within each group,  all inputs share the same input common, and all outputs share the same output common.

Group B

8-15

Group C

16-19

Fast Inputs

20-23

Inputs only – 5V or 24V. High-speed, supports quadrature encoder inputs and pulse train inputs. Each input is individually isolated.

Pin-Out

Terminal Block 1 (top)

Description

 

Pin

 

Description

Shield connection

Case

1

2

Case

Shield connection

Common for group A outputs

OutCmnA

3

4

OutCmnB

Common for group B outputs

Group A, DI/O point 0

D0

5

6

D8

Group B, DI/O point 8

Group A, DI/O point 1

D1

7

8

D9

Group B, DI/O point 9

Group A, DI/O point 2

D2

9

10

D10

Group B, DI/O point 10

Group A, DI/O point 3

D3

11

12

D11

Group B, DI/O point 11

Group A, DI/O point 4

D4

13

14

D12

Group B, DI/O point 12

Group A, DI/O point 5

D5

15

16

D13

Group B, DI/O point 13

Group A, DI/O point 6

D6

17

18

D14

Group B, DI/O point 14

Group A, DI/O point 7

D7

19

20

D15

Group B, DI/O point 15

Common for group A inputs

InCmnA

21

22

InCmnB

Common for group B inputs

Shield connection

Case

23

24

Case

Shield connection

Terminal Block 2 (bottom)

Description

 

Pin

 

Description

Shield connection

Case

1

2

Din20+

Input 20 + for 12-24 Vdc signals

Shield connection

Case

3

4

Din20+5V

Input 20 + for 5 Vdc signals

Shield connection

Case

5

6

Din20-

Input 20 – for all signals

Common for group C outputs

OutCmnC

7

8

Din21+

Input 21

Group C, DI/O point 16

D16

9

10

Din21+5V

Group C, DI/O point 17

D17

11

12

Din21-

Group C, DI/O point 18

D18

13

14

Din22+

Input 22

Group C, DI/O point 19

D19

15

16

Din22+5V

Common for group C inputs

InCmnC

17

18

Din22-

Shield connection

Case

19

20

Din23+

Input 23

Shield connection

Case

21

22

Din23+5V

Shield connection

Case

23

24

Din23-

Discrete Outputs

The D24 discrete outputs are solid state relays. The off state is high impedance, the on state is low impedance (8Ω max, 5Ω typical). Max current 75 mA. Max voltage 30 V.

Outputs can be wired in either a high-side or low-side configuration. Because all the outputs in a group share a common, all outputs in the same group must be wired the same.

The load resistance must be sized such that the maximum current through the SSR does not exceed 75 mA. The maximum current is calculated with the following equation:

Current = Vcc / RLoad

For example, if the supply voltage Vcc is 24V, and the load resistance is 480Ω, the current will be:

Current = 24Ω / 480Ω = 50mA

which is under the 75 mA limit.

Using Outputs with Inductive Loads

External fuses should be used to protect the SSRs if there is a possibility of over-current.  When switching inductive loads, it is important to place a diode or tranzorb across the load to protect the switch when transitioning from an ”ON” to an ”OFF” state. Otherwise, the collapsing magnetic field can cause a reverse voltage spike in excess of the 30 V rating of the SSR.

SSR switching inductive inductive load with high-side configuration:

When calculating the current through the SSR, use the same type of calculation as above, with the coil resistance as the load.

Discrete Inputs

To turn on a discrete input, apply a voltage of the correct level. The polarity is unimportant for inputs 0-19, and is important for 20-23.

 

 

Inputs 0-19

Inputs 20-23

Signal Levels

12-26.4 VDC

5-26.4 VDC

Max Current Draw

3 mA

7 mA

Inputs 0-19

The inputs 0-19 are polarity-independent and can be sinking or sourcing. Inputs 0-19 are divided in three groups: 0-7, 8-15, 16-19. Each group shares a common, so all inputs in a group must be wired the same.

 

Used with a sourcing output

Used with a sinking output

Inputs 20-23

Each input is individually isolated and has Din+, Din +5V,  and Din– connections. Use only Din+ or Din+5V, not both.

Example:

Differential Quadrature Wiring without Wire Break Detection

Use these wiring diagrams for encoders with the outputs listed below. The D24 will not be able to detect a broken wire with this wiring configuration.

*RS-422 will only work in this configuration if the differential output is greater than 3.5V. Some RS-422 drivers may not provide sufficient voltage.

 

With Z (Index)
5V Differential or RS-422 with differential output > 3.5V

With Z (Index)
12-24V Differential or Push-Pull 12-24V with complements

First quadrature input without Z (Index)
5V Differential or RS-422 with differential output > 3.5V

First quadrature input without Z (Index)
12-24V Differential or Push-Pull 12-24V with complements

Second quadrature input without Z (Index)
5V Differential or RS-422 with differential output > 3.5V

Second quadrature input without Z (Index)
12-24V Differential or Push-Pull 12-24V with complements

Differential Quadrature Wiring with Wire Break Detection

Use these wiring diagrams for encoders with the outputs listed below. The D24 will be able to detect a broken wire with this wiring configuration.

*RS-422 will only work in this configuration if the differential output is greater than 3.5V. Some RS-422 drivers may not provide sufficient voltage.

 

5V Differential or
RS-422 with differential output greater than 3.5V

12-24V Differential or
Push-Pull 12-24V with complements

Single-ended Quadrature Wiring

Use these wiring diagrams for encoders with the outputs listed below. The D24 will be able to detect a broken wire with this wiring configuration.

*Use RS-422 in this configuration only if the differential output is less than 3.5V. Otherwise, use the differential wiring.

 

Quadrature input with Z (Index)
TTL or 5V signal levels

Quadrature input with Z (Index)
12-24V signal levels

First quadrature input without Z (Index)
TTL or 5V signal levels

First quadrature input without Z (Index)
12-24V signal levels

Second quadrature input without Z (Index)
TTL or 5V signal levels

Second quadrature input without Z (Index)
12-24V signal levels

 

See Also

Wiring Guidelines | D24 Module


Send comments on this topic.