If new features have been added or problems fixed in the Serial or Ethernet communication modules' firmware, then it is necessary to update the firmware to take advantage of these improvements. You should only use the firmware download feature at the instruction of technical support to address a specific need.
Note: You cannot update the RMC ENET firmware when connected to the RMC via the TCP/IP Direct to RMC-ENET communication driver. You will need to use either the Serial or TCP/IP-to-RS232 Bridge driver.
To download new firmware:
Obtain the new firmware from technical support.
Start RMCWin.
Turn off the system being controlled by the RMC. This is necessary because the RMC must be reset for the new firmware to take effect. During this time, the RMC will lose communication through the communications module.
On the Tools menu, click Module Configuration.
In the Slots list, click the Ethernet or Serial module.
Click Slot Options.
Click the Firmware tab.
Click New Firmware.
After reading the warning, click OK if you feel it is a safe time to have the communications be interrupted. Otherwise, click Cancel.
You will be asked to find the file you will use as the new firmware file. In the File name box, enter the name of the firmware file provided by technical support, and click Open. This file can be on a floppy or on the hard drive.
The version numbers of the firmware to be downloaded will be displayed. Verify that the firmware date is the version you expected. If so, click Yes, otherwise, click No to select another firmware file.
The firmware will then be downloaded.
When the download is complete, click OK from the progress dialog box. Click Cancel from the Options dialog box unless you want to make changes to other configuration items.
Ethernet Firmware Files
The RMC Ethernet protocols are divided into two different firmware files. When updating the RMC100 Ethernet firmware, you must choose the file that contains the protocol you need. The files are called Protocol Group E and Protocol Group F:
New RMC100-ENET modules will be shipped with Protocol Group E. However, both groups are available for download from the Delta website, and both are supported.