The following specifications apply to the digital inputs and outputs on the CPU, Communication Digital I/O and Sensor Digital I/O modules:
Inputs (CPU 0-1 and DI/O 0-17)
CPU: Differential (Sink or Source) DI/O: Sinking (Sourcing driver) |
Logic Polarity |
CPU: True High DI/O: Configurable (True High default) |
Isolation |
2500 VAC RMS optically isolated |
Signal compatibility |
6 mA max at 5 VDC, 10 mA max at 24 VDC |
Threshold voltage |
2.75 VDC typical, 3 VDC maximum |
Threshold current |
2.7 mA typical, 3.2 mA maximum |
Max input voltage |
26.4 VDC |
Filtering |
Digital I/O Inputs 0-15: 500 µs Digital I/O Inputs 16-17: 250 µs CPU Inputs 0-1: none |
8-bit edge counter |
Input 17 |
Quadrature counter |
Inputs 16 (A input) and 17 (B input) |
Standard Outputs (DI/O module 0-7, CPU module 0-1)
Solid State Relay CPU: Independent DI/O: Common high or low side |
Logic polarity |
CPU: True High DI/O: Configurable (True high default) |
Isolation |
2500 VAC RMS |
Maximum voltage |
±30 V (DC or peak AC) |
Maximum current |
±100 mA |
Max. propagation delay |
1.5 ms |
Logic 1 |
Low impedance (50 W maximum) |
Logic 0 |
High impedance (<1 mA leakage current at 250 V) |