Link Type - Comm Trigger
Link Type:
CommTrig (C, hex 0x43, dec 67)
Link Value:
Sync Value
Range:
0 to 65,535
Note: This link type is available only in RMC100 CPU firmware version 20010123 and later.
This link type is used to synchronize execution of the step table with changes made externally from the PLC or other controlling system (called master below). This link type pauses the step-sequence execution until the master indicates it is ready by changing the Link Value or Extended Link Value. This function is useful when the master updates information in the RMC each machine cycle.
The RMC maintains an internal Extended Link Value for each axis; each is initialized on RMC power-up to 0. When the CommTrig (C) link type is encountered, the Link Value is compared with the Extended Link Value for the axis running the event sequence:
There are two ways to trigger this link type to proceed:
Note: The Extended Link Value is also used by the Skew Detection (<) link type. Care must be taken to ensure that these link types are not used on the same axis.
Note: Because the Extended Link Value powers up with 0, starting with a Comm Trigger (C) link value of 0 will cause the event sequence to wait the first time it encounters this link type.
Example:
Step 10
Step 11
Step 12
Mode
0x0000
0x0001
0x0001
Accel
10
10
Decel
10
10
Speed
1000
1000
Command Value
4000
5000
Command
G
G
Commanded Axes
Default
Default
Default
Link Type
CommTrig
BitsON
BitsON
Link Value
1
1
Link Next
11
12
10
This example is an axis making two moves. Suppose the PLC wants to control these moves by downloading the step sequence to the RMC. Here is how this can be done:
  1. Under Link Type Category, select System-wide (Basic, non-axis).
  2. Under Link Type, select Comm Trigger.
  3. Under Link Condition, enter the Sync Value you wish to start with.
  4. Click OK.
  1. Enter a 'C' into the Link Type field.
  2. Enter the Link Value.