Default: Transducer specific
Range: -32768 to 32767
This scale is used on MDT, SSI, Analog position axes with the Offset parameter and the Prescale Divisor bits of the Config word to convert the Transducer Counts to an Actual Position. Quadrature axes use this parameter with the Prescale Divisor bits to convert from the change in Transducer Counts to a change in the Actual Position. Resolver axes use this parameter together with the Count Offset to calculate the Actual Position.
For details on converting counts to position units see the appropriate topics for your transducer types:
Note: When the Scale is set to 0, it is treated as though the Scale is set to 32768. This allows a one-to-one relationship between counts and position units. Similarly, a Scale value of -32768 represents a negative one-to-one relationship between counts and position units (increasing counts mean decreasing position units).
Note: You should never set the Scale below 16383 (except for resolver axes). If it does go below that value, then use the Prescale Divisor bits in the Configuration Word. For details, refer to the discussion on scaling for your transducer type.
Note: In RMC100 CPU firmware prior to 19991216, Scale could not be 0 or -32768 for MDT, SSI, and analog transducers.