Set Profile Commands
Format: 0AAA RRRR 0010 NNNN
R Used for Status Area Request
N Used for Command Index described below
A Used only by Communication Digital I/O; 0 for PROFIBUS-DP
These commands allow the programmer to change motion profiles stored in the RMC. Only one value in one profile can be changed per axis each time the synchronization register is changed, but the profiles can be changed while the axis is moving. The new profile will be used by the next Go Using Profile command specifying that profile. Recall that new Go and Go Using Profile commands can be given while the axis is moving.
The format of the Command Register for the Set Profile commands is given below:
     1111|11  |    |
BIT# 5432|1098|7654|3210
HEX      |SAR |CMND|INDX
VALUE-------------------
0X20 0AAA|XXXX|0010|0000 SET PROFILE 0, 4, 8 or 12 MODE
0X21 0AAA|XXXX|0010|0001 SET PROFILE 0, 4, 8 or 12 ACCEL
0X22 0AAA|XXXX|0010|0010 SET PROFILE 0, 4, 8 or 12 DECEL
0X23 0AAA|XXXX|0010|0011 SET PROFILE 0, 4, 8 or 12 SPEED
0X24 0AAA|XXXX|0010|0100 SET PROFILE 1, 5, 9 or 13 MODE
0X25 0AAA|XXXX|0010|0101 SET PROFILE 1, 5, 9 or 13 ACCEL
0X26 0AAA|XXXX|0010|0110 SET PROFILE 1, 5, 9 or 13 DECEL
0X27 0AAA|XXXX|0010|0111 SET PROFILE 1, 5, 9 or 13 SPEED
0X28 0AAA|XXXX|0010|1000 SET PROFILE 2, 6, 10 or 14 MODE
0X29 0AAA|XXXX|0010|1001 SET PROFILE 2, 6, 10 or 14 ACCEL
0X2A 0AAA|XXXX|0010|1010 SET PROFILE 2, 6, 10 or 14 DECEL
0X2B 0AAA|XXXX|0010|1011 SET PROFILE 2, 6, 10 or 14 SPEED
0X2C 0AAA|XXXX|0010|1100 SET PROFILE 3, 7, 11 or 15 MODE
0X2D 0AAA|XXXX|0010|1101 SET PROFILE 3, 7, 11 or 15 ACCEL
0X2E 0AAA|XXXX|0010|1110 SET PROFILE 3, 7, 11 or 15 DECEL
0X2F 0AAA|XXXX|0010|1111 SET PROFILE 3, 7, 11 or 15 SPEED
Notice that for each command, four different profile numbers are listed. The actual profile affected is determined by the axis issuing the command. The following chart shows which commands affect which profiles when issued on a particular axis. Notice that an RMC100-M1-PROFI can only set the first eight (8) profiles:
COMMAND
AXIS 0
AXIS 1
AXIS 2
AXIS 3
0x20-0x23
4
8
12
0x24-0x27
1
5
9
13
0x28-0x2B
2
6
10
14
0x2C-0x2F
3
7
11
15
The command data represents the value of the field to be set in the profile.
We wish to set profiles 2 and 7 with the following values:
PROFILE 2
PROFILE 7
MODE
0x0001
0x0001
ACCEL
100
150
DECEL
70
70
SPEED
12000
20000
Looking at the chart above, we can see that we issue Set Profile commands to axis 0 to set profile 2 and we use axis 1 Set Profile commands to set profile 7. Therefore, we can do both at the same time. This would take four scans because we can send one word of each profile on each axis per scan:
First scan:
O+1
0X28h
(Set profile 2 MODE)
O+2
0001h
(Value of profile 2 MODE)
O+3
0X2Ch
(Set profile 7 MODE)
O+4
0001h
(Value of profile 7 MODE)
Second scan:
O+1
0X29h
(Set profile 2 ACCEL)
O+2
100
(Value of profile 2 ACCEL)
O+3
0X2Dh
(Set profile 7 ACCEL)
O+4
150
Third scan:
O+1
0X2Ah
(Set profile 2 DECEL)
O+2
70
(Value of profile 2 DECEL)
O+3
0X2Eh
(Set profile 7 DECEL)
O+4
70
Fourth scan:
O+1
0X2Bh
(Set profile 2 SPEED)
O+2
12000
(Value of profile 2 SPEED)
O+3
0X2Fh
(Set profile 7 SPEED)
O+4
20000
Example for Digital I/O:
We wish to set profile 7 to the following values:
PROFILE 7
MODE
0x0001
ACCEL
100
DECEL
70
SPEED
12000
Looking at the chart above, we can see that Set Profile commands must be to axis 1 to set profile 7. Therefore, we send the following commands:
First Command:
  0001|XXXX|0010|1000 (1X28) Set profile 7 Mode
Receive after Acknowledge:
            XXXX|XXXX (XX) Low byte of requested data
  0000|0000|0000|0001 (0000) Profile 7 Mode
            XXXX|XXXX (XX) High byte of requested data
Second Command:
  0001|XXXX|0010|1001 (1X29) Set profile 7 Speed
  0000|0000|0110|0100 (0064) Profile 7 Speed
Third Command:
  0001|XXXX|0010|1010 (1X2A) Set profile 7 Decel
  0000|0000|0100|0110 (0046) Profile 7 Decel
Fourth Command:
  0001|XXXX|0010|1011 (1X2B) Set profile 7 Speed
  0010|1110|1110|0000 (2EE0) Profile 7 Speed