Get Profile Commands
Format: 0AAA 0000 1010 NNNN
N Used for Command Index described below
A Used only by Communication Digital I/O; 0 for PROFIBUS-DP
These commands allow the programmer to retrieve the RMC’s stored motion profiles. Only one value in one profile can be read per axis each time the synchronization register is changed
The format of the Command Register for the Get Profile commands is given below:
Note: The Status Area Request area (bits 8-11) of the command and the command data are ignored.
     1111|11  |    |
BIT# 5432|1098|7654|3210
HEX      |    |CMND|INDX
VALUE-------------------
0XA0 0AAA|XXXX|1010|0000 GET PROFILE 0, 4, 8 or 12 MODE
0XA1 0AAA|XXXX|1010|0001 GET PROFILE 0, 4, 8 or 12 ACCEL
0XA2 0AAA|XXXX|1010|0010 GET PROFILE 0, 4, 8 or 12 DECEL
0XA3 0AAA|XXXX|1010|0011 GET PROFILE 0, 4, 8 or 12 SPEED
0XA4 0AAA|XXXX|1010|0100 GET PROFILE 1, 5, 9 or 13 MODE
0XA5 0AAA|XXXX|1010|0101 GET PROFILE 1, 5, 9 or 13 ACCEL
0XA6 0AAA|XXXX|1010|0110 GET PROFILE 1, 5, 9 or 13 DECEL
0XA7 0AAA|XXXX|1010|0111 GET PROFILE 1, 5, 9 or 13 SPEED
0XA8 0AAA|XXXX|1010|1000 GET PROFILE 2, 6, 10 or 14 MODE
0XA9 0AAA|XXXX|1010|1001 GET PROFILE 2, 6, 10 or 14 ACCEL
0XAA 0AAA|XXXX|1010|1010 GET PROFILE 2, 6, 10 or 14 DECEL
0XAB 0AAA|XXXX|1010|1011 GET PROFILE 2, 6, 10 or 14 SPEED
0XAC 0AAA|XXXX|1010|1100 GET PROFILE 3, 7, 11 or 15 MODE
0XAD 0AAA|XXXX|1010|1101 GET PROFILE 3, 7, 11 or 15 ACCEL
0XAE 0AAA|XXXX|1010|1110 GET PROFILE 3, 7, 11 or 15 DECEL
0XAF 0AAA|XXXX|1010|1111 GET PROFILE 3, 7, 11 or 15 SPEED
Notice that for each command, four different profile numbers are listed. The actual profile read is determined by the axis issuing the command. The following chart shows which profile is affected by a given command on a given axis. Notice that an RMC100-M1-PROFI can only get the first eight (8) profiles:
COMMAND
AXIS 0
AXIS 1
AXIS 2
AXIS 3
0XA0-0XA3
4
8
12
0XA4-0XA7
1
5
9
13
0XA8-0XAB
2
6
10
14
0XAC-0XAF
3
7
11
15
The data returned where the Status Area Request data would be returned is the requested profile field.
We wish to get profiles 2 and 7 into the RMC. Looking at the chart above, we can see that we issue Get Profile commands to axis 0 to get profile 2 and we use axis 1 Get Profile commands to get profile 7. Therefore, we can do both at the same time. Suppose that the RMC had the following values for profiles 2 and 7:
PROFILE 2
PROFILE 7
MODE
0x0001
0x0001
ACCEL
100
150
DECEL
70
70
SPEED
12000
20000
This would take at least five scans because we can get one word of each profile on each axis per scan:
First scan:
O+1
00A8h
(Get profile 2 MODE)
O+2
XXXXh
(Unused)
O+3
00ACh
(Get profile 7 MODE)
O+4
XXXXh
(Value of profile 7 MODE)
Second scan:
After the Synchronization Output register is incremented, the RMC will process the commands and update the Synchronization Input register to match. At this time, the input registers would hold the following values:
I+1
XXXXh
(Axis 0 STATUS)
I+2
0001h
(Profile 2 MODE)
I+3
XXXXh
(Axis 1 STATUS)
I+4
0001h
(Profile 7 MODE)
We can now send the second set of requests:
O+1
00A9h
(Get profile 2 ACCEL)
O+2
XXXXh
(Unused)
O+3
00ADh
(Get profile 7 ACCEL)
O+4
XXXXh
(Unused)
Third scan:
I+1
XXXXh
(Axis 0 STATUS)
I+2
100h
(Profile 2 ACCEL)
I+3
XXXXh
(Axis 1 STATUS)
I+4
150h
(Profile 7 ACCEL)
We can now send the third set of requests:
O+1
00AAh
(Get profile 2 DECEL)
O+2
XXXXh
(Unused)
O+3
00AEh
(Get profile 7 DECEL)
O+4
XXXXh
(Unused)
Fourth scan:
I+1
XXXXh
(Axis 0 STATUS)
I+2
70h
(Profile 7 DECEL)
I+3
XXXXh
(Axis 1 STATUS)
I+4
70h
(Profile 7 DECEL)
We can now send the fourth set of requests:
O+1
00ABh
(Get profile 2 SPEED)
O+2
XXXXh
(Unused)
O+3
00AFh
(Get profile 7 SPEED)
O+4
XXXXh
(Unused)
Fifth scan:
I+1
XXXXh
(Axis 0 STATUS)
I+2
12000h
(Profile 7 SPEED)
I+3
XXXXh
(Axis 1 STATUS)
I+4
12000h
(Profile 7 SPEED)
Example for Digital I/O:
We wish to get profile 7 into the RMC. Looking at the chart above, we can see that we issue Get Profile commands to axis 1 to get profile 7. Suppose that the RMC had the following values for profile 7:
PROFILE 7
MODE
0x0001
ACCEL
100
DECEL
70
SPEED
12000
The following steps would be taken to read profile 7:
First Command:
  0001|0000|1010|1000 (10A8) Get Profile 7 Mode
Receive after Acknowledge:
            0000|0001   (01) Low byte of Mode
  XXXX|XXXX|XXXX|XXXX (XXXX) Unused
            0000|0000   (00) High byte of Mode
Second Command:
  0001|0000|1010|1001 (10A9) Get Profile 7 Accel
            0110|0100   (64) Low byte of Accel
            0000|0000   (00) High byte of Accel
Third Command:
  0001|0000|1010|1010 (10AA) Get Profile 7 Decel
            0100|0110   (46) Low byte of Decel
            0000|0000   (00) High byte of Decel
Fourth Command:
  0001|0000|1010|1011 (10AB) Get Profile 7 Speed
            1110|0000   (E0) Low byte of Speed
            0010|1110      (2E) High byte of Speed